Skip to Content.
Sympa Menu

sphenix-magnet-l - [Sphenix-magnet-l] FW: using "double extra strong" (WCB)?

sphenix-magnet-l AT lists.bnl.gov

Subject: sPHENIX discussion of the superconducting solenoid

List archive

Chronological Thread  
  • From: "Yip, Kin" <kinyip AT bnl.gov>
  • To: "sphenix-magnet-l AT lists.bnl.gov" <sphenix-magnet-l AT lists.bnl.gov>
  • Subject: [Sphenix-magnet-l] FW: using "double extra strong" (WCB)?
  • Date: Sun, 13 Mar 2022 12:21:29 +0000

For the record.

Kin


-------- Original message --------
From: "Yip, Kin" <kinyip AT bnl.gov>
Date: 3/11/22 09:47 (GMT-05:00)
To: "Karl, Robert F" <rkarl AT bnl.gov>
Cc: "Chan, David" <dchan AT bnl.gov>
Subject: RE: using "double extra strong" ?

Thanks a lot for the confirmation !!

 

From: Karl, Robert F <rkarl AT bnl.gov>
Sent: Friday, March 11, 2022 9:38 AM
To: Yip, Kin <kinyip AT bnl.gov>
Cc: Chan, David <dchan AT bnl.gov>
Subject: RE: using "double extra strong" ?

 

Hi Kin,

 

The 4 WCB pipes that we are using to power sPHENIX are all “double extra strong” as per Dave Phillips request.

 

Thanks,

Rob

 

From: Yip, Kin <kinyip AT bnl.gov>
Sent: Thursday, March 10, 2022 11:13 PM
To: Karl, Robert F <rkarl AT bnl.gov>
Cc: Chan, David <dchan AT bnl.gov>
Subject: using "double extra strong" ?

 

Dear Rob,

 

Below was the email from D. Phillips about the diameters and resistance of the water-cooled-bus (WCB) etc.

 

For the water-cooled-busses you’ve connected from 1008B, have you used  the “double extra strong” WCB

(instead of “extra strong”) ?  [  In another email series, we decided to use “double extra strong” to go for the least resistance. ]

 

Can you please let me know ??

 

Kin

 

From: Phillips, David B <phillips AT bnl.gov>
Sent: Thursday, April 19, 2018 1:43 PM
To: Schultheiss, Carl <carls AT bnl.gov>
Cc: Streckenbach, Brian <bstreckenbach AT bnl.gov>; Yip, Kin <kinyip AT bnl.gov>; Rosas, Pablo J <rosas AT bnl.gov>; Giannotti, Paul <gia AT bnl.gov>; Mills, James A <mills AT bnl.gov>
Subject: PHENIX existing WCB

 

There are 4 pairs of copper water cooled bus from 1008B to 1008-IR.

2 pairs of 2” extra strong

2 pairs of 2” double extra strong

 

2” extra strong:

OD = 2.375”

ID = 1.933”

Wall thickness = 0.221”

Area = 1.49 sq in

Resistance at 20C = 5.53 micro-Ohms/ft

Resistance at 65C = 6.38 micro-Ohms/ft

Resistance at 350’ (at 65C) = 0.0022 Ohms

 

2” double extra strong:

OD = 2.375”

ID = 1.503”

Wall thickness = 0.436”

Area = 2.66 sq in

Resistance at 20C = 3.11 micro-Ohms/ft

Resistance at 65C = 3.59 micro-Ohms/ft

Resistance at 350’ (at 65C) = 0.0013 Ohms

 

I think the actual length will be less than 350’.

Actual operating temperature should be below 50C.

For one set of 2” double extra strong WCB the required water flow at 4800A and 20F temperature rise is 10.3 gpm (this flow is achievable, velocity is 1.9 ft/s).

 

Photo of the WCB where it exits 1008B attached.

The cooling water has two paths in the bus, one direction cools the bus from 1008B to the magnet, the other direction cools the bus from the wall of 1008B to the power supply and is the cooling water for the power supply. This can be modified for sPHENIX.

 

David Phillips

Building 911B

Upton, NY 11973

631-344-4671, Fax 631-344-5954, Cell 631-804-9477

On site pager 344-3456 then 4267 then your number

 



  • [Sphenix-magnet-l] FW: using "double extra strong" (WCB)?, Yip, Kin, 03/13/2022

Archive powered by MHonArc 2.6.24.

Top of Page