sphenix-magnet-l - [Sphenix-magnet-l] status ... (pressure test/leak check) ... PLC sent too much current and burnt the positioner

sphenix-magnet-l AT lists.bnl.gov

Subject: sPHENIX discussion of the superconducting solenoid

List archive

Chronological Thread  
  • From: "Yip, Kin" <kinyip AT bnl.gov>
  • To: "sphenix-magnet-l AT lists.bnl.gov" <sphenix-magnet-l AT lists.bnl.gov>
  • Subject: [Sphenix-magnet-l] status ... (pressure test/leak check) ... PLC sent too much current and burnt the positioner
  • Date: Mon, 8 Feb 2016 17:42:27 +0000

Hi,

 

1.      Because of the snow, we may have been slowed down by 1 day or so.   The Cryo group

is still trying to tighten all the pipes/valves during their pressure test/leak check.  They plan

to do the official pressure test/leak check with Mike Gaffney (with the help of the vacuum

group --- they had set up the leak detector already in 912 for us).

 

  1.1 After that, Sonny and Co. can do the hypot/impulse tests as in the pre-test Inspection traveler.

 

2.      I attach 2 sets of emails sent to me by Roberto last week and today.   Apparently, the PLC put out 250 mA instead of 20 mA

which seemed to have burnt the circuit/fuse of the positioner --- which is used to close/open the valve to mix the hot and cold

gas.    Roberto told me that they might be able to live without knowing whether the valve is closed or half closed but they have to

fix the PLC so that it’ll not continue to damage the circuit ….

 

3.      Pat Talty hasn’t come to help us yet but Roberto hopes that Pat can help us enough this week so that we may finish the control system

for cool-down by Friday so that we may start cooling down !!!

 

Kin

 

From: Than, Yatming (Roberto)
Sent: Monday, February 08, 2016 12:00 PM
To: Yip, Kin <kinyip AT bnl.gov>
Subject: FW: siemens positioner pictures attached 6DR8104-8N

 

Kin,

The I/P are arriving today, if they get delivered.

Pressure test we will try to do the gross leak check this afternoon and the real one tomorrow.

The PLC card was putting out 250 mA, instead of 20 mA.

That end still to resolve.

 

Roberto

 

From: Tallerico, Thomas N
Sent: Monday, February 08, 2016 11:28 AM
To: Victor Ancelson (victor AT priinc.com)
Cc: Masi Jr, Leonard; Zhang, Yi; Meier, Richard; Nace II, David; Moore, John J; Than, Yatming (Roberto); Orfin, Paul; Soria, Victor
Subject: siemens positioner pictures attached 6DR8104-8N

 

I think we damaged this card. (see pictures). Are these PC cards available for purchase? They are surface mount PC cards. No positioners or valves appear to be working. Some areas on the cards appear scorched. Thanks Tom Tallerico

 

 

 

 

 

From: Than, Yatming (Roberto)
Sent: Thursday, February 04, 2016 5:33 PM
To: Yip, Kin <kinyip AT bnl.gov>
Subject: VALVEBOX SIEMENS POSTIONERS

 

 

 

Kin,

When we tried cycling the valves from the PLC they would not work.

We check them out earlier with independent control signal, 4-20 mA generator, and the valves cycled.

Turns out they burned out the input circuit/or fuse on the input circuit Siemens positioners.

The control signal they sent from rack was way above the 20 mA (70 mA), some wiring issue between PLC analog card and power supply.

 

 

So they ordered I/P [current to pressure] transmitters to replace the positioners.

At least we can control the valves, but will not know exactly how much they are actually open.

 

If they come in on Monday we need to  replace the Siemens positioners.

 

 

Always something.

 

Also they will shutdown instrument air Friday afternoon.

I ask to get the air back for Tuesday so I can restart cryoplant

 

 

Roberto

 

 

 

 

 

 

 

 

Attachment: IMG_20160208_105102371_HDR.JPG
Description: IMG_20160208_105102371_HDR.JPG

Attachment: IMG_20160208_105124443.jpg
Description: IMG_20160208_105124443.jpg

Attachment: IMG_20160208_105135535.jpg
Description: IMG_20160208_105135535.jpg

Attachment: IMG_20160208_105309125_HDR.JPG
Description: IMG_20160208_105309125_HDR.JPG

Attachment: IMG_20160208_105318575.jpg
Description: IMG_20160208_105318575.jpg

Attachment: IMG_20160208_105738517_HDR.JPG
Description: IMG_20160208_105738517_HDR.JPG