Hi,
Can we run the PLC to see if we have any further Watch Dog Timer issues?
Carl
From: Yip, Kin <kinyip AT bnl.gov>
Sent: Monday, November 4, 2024 6:32 PM
To: Schultheiss, Carl <carls AT bnl.gov>; Zubarriain, Jonathan <jzubarria AT bnl.gov>
Cc: Costanzo, Timothy <tcostanzo AT bnl.gov>; sphenix-magnet-l AT lists.bnl.gov
Subject: RE: sphenix watch dog timer fault
Dear Carl,
You probably already assumed what I am going to say below. I went to talk with Tim Costanzo this evening (in his CAS shift this evening).
He told me that the 24 V connection was so loose that it could cause problem even when there is no (relatively) violent action of closing/opening the door. Though there is no way to prove,
Tim agrees that this loose connection could very well be the cause of the two mysterious Watchdog Timer interlocks (=> Magnet trips) that we’ve observed during the 2024 run (~6 months).
Richard (CAS) blamed me for not providing him this observation (opening/closing door => cause Watchdog Timer interlocks every time) such that he didn’t know to check about this location of wiring a
few months ago 😅 Well, I wasn’t fully aware of this and didn’t think of its significance because the Watchdog Timer interlock change is not important when we open/close the PS door (as the Magnet is
off, at 0 A). We asked Tim to check after we/I saw this happened too often and we didn’t understand why this interlock should trip when the PS door closes/opens.
Kin
From: Yip, Kin
Sent: Monday, October 28, 2024 5:38 AM
To: Costanzo, Timothy <tcostanzo AT bnl.gov>; Rosas, Pablo J <rosas AT bnl.gov>
Cc: Schultheiss, Carl <carls AT bnl.gov>; Karl, Robert F <rkarl AT bnl.gov>; Moloney, John <jmoloney AT bnl.gov>
Subject: RE: sphenix watch dog timer fault
Thanks a lot. I wonder whether this loose connection might have caused problems (like twice in the last 6 months) when you didn't open and close the door ?! 🤔
Kin
-------- Original message --------
From: "Costanzo, Timothy" <tcostanzo AT bnl.gov>
Date: 10/27/24 22:29 (GMT+00:00)
To: "Rosas, Pablo J" <rosas AT bnl.gov>
Cc: "Yip, Kin" <kinyip AT bnl.gov>, "Schultheiss, Carl" <carls AT bnl.gov>, "Karl, Robert F" <rkarl AT bnl.gov>, "Moloney, John" <jmoloney AT bnl.gov>
Subject: sphenix watch dog timer fault
Hi Pablo
John and I found that the sphenix PS watch dog timer fault was being caused by a loose connection on the 24VDC (PS #5) din rail. We could see the fault come in when the door was opened and closed. We tighten the din rails screws, and tested, all seems okay now.
I will see you Tuesday.
Thanks Tim
-
RE: [[Sphenix-magnet-l] ] sphenix watch dog timer fault,
Yip, Kin, 11/04/2024
-
RE: [[Sphenix-magnet-l] ] sphenix watch dog timer fault,
Schultheiss, Carl, 11/05/2024
-
Re: [[Sphenix-magnet-l] ] sphenix watch dog timer fault,
Costanzo, Timothy, 11/05/2024
- RE: [[Sphenix-magnet-l] ] sphenix watch dog timer fault, Schultheiss, Carl, 11/05/2024
-
Re: [[Sphenix-magnet-l] ] sphenix watch dog timer fault,
Costanzo, Timothy, 11/05/2024
- <Possible follow-up(s)>
- RE: [[Sphenix-magnet-l] ] sphenix watch dog timer fault, Yip, Kin, 11/05/2024
-
RE: [[Sphenix-magnet-l] ] sphenix watch dog timer fault,
Schultheiss, Carl, 11/05/2024
Archive powered by MHonArc 2.6.24.