Hi Mike Capotosto & all,
I'm forwarding info on the readout crate power interlock which exists on the IST and FGT (and I believe GMT too) readout crates. We will want this to be connected to the interlock system at STAR for the actual FST installation. In the meanwhile for lab testing you have to cheat it appropriately or the crate won't work.
(Zhenyu, maybe you can say sometime if the crate at Chicago has this interlock? We should get it added if not, so it can be a proper spare for FST. It should be low cost to add it.)
See just the last page of the attachment for wiring and function diagram. Sincerely,

Gerard



-------- Forwarded Message --------
Subject: Re: FW: Interlock installation: Delivery follow up
status...FYI
Date: Tue, 1 Nov 2011 15:55:53 -0400
From: Paul Staffan <pstaffan AT wiener-us.com>
To: D'Agostino, Ciro <cirod AT bnl.gov>
CC: Gerard Visser <gvisser AT indiana.edu>, Asselta, Kenneth <kasselta AT bnl.gov>, Christie, William <christie AT bnl.gov>, pstaffan AT wiener-us.com <'pstaffan AT wiener-us.com'>, Jim Thomas <jhthomas AT lbl.gov>, Soja, Robert <soja AT bnl.gov>



Hi Ciro, everyone,

Find attached the manual for interlock..  I am sending out the 6 cables today to Ken's attention.  Ken will receive an email shortly with all the tracking information.

Regarding Interlock, this protocol requires a 5 V supply.  Whereas Inhibit requires only a contact closure, (open or short).  I have requested clarification regarding the inhibit function and have not received confirming information from the factory regarding its use as an alternative to Interlock, (they were on a holiday yesterday).

If you prefer a relay contact closure, I do not see why we cannot provide an additional choice for Interlock, "type" features by using inhibit.  Upon my observation both options seemed to operate the same.

Since you are under a strict deadline I have released the installation doc specifying _only _the Interlock upgrade instructions.  If you like, I can also provide instructions for inhibit option later.

Please advise any comments

Have a good afternoon

Paul Staffan
Sales and Support Engineer
W-IE-NE-R Plein and Baus, Corp
300 East Auburn Ave.
Springfield, OH 45505
937-324-2420, fax 937-324-2425
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.wiener-2Dus.com&d=DwID-g&c=aTOVZmpUfPKZuaG9NO7J7Mh6imZbfhL47t9CpZ-pCOw&r=8ygAAI6gQzVe9hFCRdEAO5MwBJh2ID34fiwLpV3P1Xo&m=bAv5vA-1kRln6zOR2EsqC19QIhEq7ZD-Cpkj48FkLZs&s=U-WWZQPHMWvE8awC_nrF7luvNNjwd-6HRyPwsUgNmoI&e=

On 10/28/2011 1:27 PM, D'Agostino, Ciro wrote:

Hi Gerard,

I just spoke with Paul Staffan today, regarding confirmation of next week’s delivery date. Paul stated that he received both written, and an E-mail, confirmation that these items will definitely ship out today. Therefore, “we” are still on track for delivery to Paul next Tuesday (11/1/11), most likely late in the day.

I will be calling Paul late next Tuesday to confirm him receiving these items. Afterwards, Paul said that he will send them out right away to Ken and I, via ground shipment.

Paul is presently working on/finishing up his testing and write up of the user’s manual, which “we” should have before the items reach BNL. All o f us can then review, and post any potential questions to Paul if needed.

Lastly, Paul is also going to characterize, in his lab\setup, the nominal current draw that the interlock will want to draw. Of course “we” expect this current to be low. However, I asked for this so Ken is able to order a brick supply with an available source current that is adequate (i.e. Don’t want to order a supply capable of delivering 2 Amps when, say ,0.50A is more than enough).

-Regards,

-ciro

*Ciro A. D'Agostino, P.E.*

Project I Engineer

*Brookhaven National Laboratory*

Physics Building 510

631-344-3687

*From:*D'Agostino, Ciro
*Sent:* Wednesday, October 26, 2011 11:12 AM
*To:* Gerard Visser
*Cc:* Asselta, Kenneth; Christie, William; 'pstaffan AT wiener-us.com'; Jim Thomas; Soja, Robert
*Subject:* Interlock installation: Summary of yesterday's discussions...FYI
*Importance:* High

Hi Gerard,

                Yesterday Ken and I spoke in depth with Paul Staffan, from Wiener, regarding the pending order placed for 6 boards that will result in interlock capability of your applicable power supplies. These supplies, as Ken and I understand are…

-Wiener S/N: 3791069, MOD# MPOD, P/N: 0P09.0026U (Presently in clean room at
BNL)

-Wiener S/N: 1889018, MOD# MPOD, P/N: 0P09.0026U (Presently at BNL in rack
2C9)

-Wiener S/N: 3791068, MOD# MPOD, P/N: 0P09.0026U (Presently in clean room at
ANL)

We confirmed with Paul Staffan that the due date for these items is the first week in December 2011, which means that these items need to arrive no later than the last week in November 2011. Paul stated that this should not be an issue.

In addition, Ken and I also confirmed the following with Paul Staffan regarding part of the  interface details for these interlock boards…

-Power supply enclosures have knock-outs on front panel where the interlock boards would reside

-Interlock boards have a DSUB female 15-pin connector, of which two pins, power and ground, are facilitated

-STSG will need to build a cable from the Alan Bradley Interlock panel, to each of these interlock power supplies. Ken will reach out to Jim Thomas to confirm location of the Alan Bradley Interlock panel. In addition, Ken will reach out to you (i.e. Gerard) to note the final location for the two power supplies having the interlock, so that Ken can determine the required cable length, of which one side would connect to the supply interlocks, which will need to terminate to a DSUB male 15 pin connector, and the other side  will be terminated to a TBD connector on the Alan Bradley Interlock panel...Ken also to confirm this connector type with Jim Thomas

-Ken and I also communicated the desired interlock sense, that we confirmed with you (i.e. Gerard) yesterday, which was that when the relay is closed, the power supply shall be able to stay on, and when the relay is open the power supply shall not be able to stay...Paul will configure and test accordingly

-Ken will order a 5VDC brick power supply to drive\power this interlock via the applicable relay that you (i.e. Gerard) stated yesterday will be used in the interlock scheme, before first week of December 2011

-Lastly, I will be calling Paul this Friday morning to confirm that the interlock order placed by Ken is still on schedule for delivery next Tuesday to Paula Staffan, after of which Paul will ship to BNL via ground.

The following are other details that STSG will need to have clarified…

                (Question for Gerard)

-Does your architecture require separated 5VDC brick power supplies for each of the two interlock power supplies, or can a single brick power supply feed multiple interlock power supplies

(Question for Paul Staffan)

-What is the maximum interlock circuit board D.C. current draw? We are expecting this to be low, but thought it would be good to verify, and ensure the selected 5VDC power supply source current capability will be appropriately sized.

-Regards,

-Ciro

*Ciro A. D'Agostino, P.E.*

Project I Engineer

*Brookhaven National Laboratory*

Physics Building 510

631-344-3687

Attachment: Interlock upgrade to PS- STAR MPOD_PCI CRATE.pdf