Skip to Content.
Sympa Menu

star-qaboard-l - [STAR-QAboard] TPC issues

star-qaboard-l@lists.bnl.gov

Subject: STAR QA Board

List archive

Chronological Thread  
  • From: videbaek <videbaek@bnl.gov>
  • To: Star-qaboard L <star-qaboard-l@lists.bnl.gov>
  • Subject: [STAR-QAboard] TPC issues
  • Date: Sun, 19 Jul 2020 13:26:41 -0400


Hi

Just to bring to attention that the TPC airflow compressor stopped working yesterday around 5 pm,
with subsequent higher temperatures and humidity level above the desired 42-43%. This has consequences
for the quality of data due to the inner/outer field cage current as Gene as discussed earlier
See attached plot of the humidity in TPC air in the last ~24 hours

Alexei L. and Tim C went in today to try to fix today around noon
see their note from the e-log

"TPC IFC blower: Compressor does not stay engaged, intermittently turns on/off.
Replaced adjusting current trip contactor: Same issue
Replaced 24V contactor: same issue

It seems like the problem might be with the compressor. Will have to have CAD HVAC technicians check compressor and charge levels.
Unit is set to run with compressor off at the moment."



--
Flemming Videbaek
senior scientist
videbaek @ bnl.gov
Brookhaven National Lab
Physics Department
Bldg 510D
Upton, NY 11973

phone: 631-344-4106
cell : 631-681-1596

Attachment: Screen Shot 2020-07-19 at 13.24.26.png
Description: PNG image



  • [STAR-QAboard] TPC issues, videbaek, 07/19/2020

Archive powered by MHonArc 2.6.24.

Top of Page