Hi Zhenyu,
I am not sure what additional tests you are proposing? 3M gave a limit for water content, and measurements by experts found it was very low. So do you trust this advice and measurements or not?
best Flemming
On 2021-10-20 16:20, Ye, Zhenyu wrote:
The reason that I propose to use the new barrels in Run22 is to avoid
having any potential problem in the middle of the run.
The opened drum has been in its current status in 6 years so it will
not make a big difference to let it sit for another 6 months (let me
know if you think otherwise). We will have plenty of time to test use
it in the summer and continue using it in Run23 and beyond if no
problem is found.
Zhenyu
On Oct 20, 2021, at 3:13 PM, Sharma, Rahul <rsharma AT bnl.gov> wrote:
I agree with Elke
* Rahul
From: Star-fst-l <star-fst-l-bounces AT lists.bnl.gov> On Behalf Of
Aschenauer Elke-Caroline
Sent: Wednesday, October 20, 2021 4:12 PM
To: Ye, Zhenyu <yezhenyu AT uic.edu>
Cc: Star-fst L <star-fst-l AT lists.bnl.gov>
Subject: Re: [Star-fst-l] NOVEC from the opened drum is good to use
sorry, maybe Iām on the wrong track, but would it not be better to
use the open NOVEC as fast as possible to avoid that it gets water
in it.
Cheers elke
On Oct 20, 2021, at 15:59, Ye, Zhenyu <yezhenyu AT uic.edu> wrote:
Thank you for the efforts, Prithwish.
I would propose to continue using the small barrels of new NOVEC for
run 22, and use the NOVEC from the opened drum from PHENIX towards
the end of the run or in the summer.
Zhenyu
On Oct 20, 2021, at 2:34 PM, Tribedy, Prithwish <ptribedy AT bnl.gov>
wrote:
Hello Everyone,
Good news!! The report from the chemistry lab has arrived. The
water contamination in the remaining NOVEC liquid from the opened
drum is well below 90 ppm (as required for safe operations according
to the 3M experts).
We provided the chemists with three samples: 1) from the top layer
of the opened drum (Sample A TOP), 2) from the bottom of the opened
drum (Sample B BOT) and, 3) from a newly opened small NOVEC
container (Sample C SML). All the samples have been checked twice
and found to have water contaminations at the level of 41-44 ppm.
This level of contamination is permissible for safe operations as
per our previous communication with the 3M experts.
So, we can go ahead and use the NOVEC from the opened drum for the
upcoming run.
We're grateful to our colleagues from the Neutrino and Nuclear
Chemistry group of the Chemistry Department at BNL.
Regards,
Prithwish
Prithwish Tribedy
Physics Department, Brookhaven National Laboratory
Upton, NY 11973, USA
Phone: 631-344-8904, 631-344-3853
E-mail: ptribedy AT bnl.gov
Begin forwarded message:
From: "Gokhale, Sasmit" <sgokhale AT bnl.gov>
Subject: Water content analysis of C4F9OC2H5 coolant liquid
Date: October 20, 2021 at 2:28:28 PM EDT
To: Prithwish Tribedy <ptribedy AT icloud.com>, "Yeh, Minfang"
<yeh AT bnl.gov>
Cc: "Hu, Yu" <yuhu AT bnl.gov>
Hello Prithwish,
I hope you are doing well. I have finished analyzing the three
samples that you gave us. I ran two Karl Fischer titration
measurements for each of the three bottles that you provided i.e.
one sample was collected from the top and bottom of the each bottle.
Below are the results:
Sample A BOT:
Measurement 1: water content = 43.98 ppm
Measurement 2: water content = 44.89 ppm
Sample B TOP:
Measurement 1: water content = 42.22 ppm
Measurement 2: water content = 43.23 ppm
Sample C SML:
Measurement 1: water content = 41.98 ppm
Measurement 2: water content = 41.79 ppm
To check the accuracy, I also ran a sample of one of our organic
solvents which should have a water content between 60 to 80 ppm and
the measured water quantity for that liquid was 63.18 ppm. So it
seems the measured values can be trusted.
Please let me know if you have any further questions.
Best Regards,
Sasmit
Sasmit Gokhale
Research Associate
Brookhaven National Lab
Building 555
Upton, NY 11973
Phone: 631-344-4992
Email: sgokhale AT bnl.gov
<image001.png>
_______________________________________________
Star-fst-l mailing list
Star-fst-l AT lists.bnl.gov
https://lists.bnl.gov/mailman/listinfo/star-fst-l [1]
_______________________________________________
Star-fst-l mailing list
Star-fst-l AT lists.bnl.gov
https://lists.bnl.gov/mailman/listinfo/star-fst-l
_Note: Please do not feel obligated to respond to this message outside
of your work hours._
( `,_' )+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-
) `\ +
/ '. | Elke-Caroline Aschenauer (she/her/hers) =
| `, -
\,_ `-/ Brookhaven National Lab +
,&&&&&V Physics Dept., 25 Corona Road =
,&&&&&&&&: Bldg. 510 /2-195 Rocky Point, NY, -
,&&&&&&&&&&; 20 Pennsylvania Avenue 11778 +
| |&&&&&&&;\ Upton, NY 11973
=
| | :_) _ Tel.: 001-631-344-4769 Tel.: +1-631-569-4290
-
| | ;--' | Cell-USA: +1-757-2565224
+
'--' `-.--. | Cell-Europe:
+49152220025211 =
\_ | |āā
-
`-._\__/ Mail: elke AT bnl.gov elke.caroline AT me.com
+
+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=-+=
_______________________________________________
Star-fst-l mailing list
Star-fst-l AT lists.bnl.gov
https://lists.bnl.gov/mailman/listinfo/star-fst-l
Links:
------
[1] https://lists.bnl.gov/mailman/listinfo/star-fst-l
_______________________________________________
Star-fst-l mailing list
Star-fst-l AT lists.bnl.gov
https://lists.bnl.gov/mailman/listinfo/star-fst-l
--
Flemming Videbaek
senior scientist
videbaek @ bnl.gov
Brookhaven National Lab
Physics Department
Bldg 510D
Upton, NY 11973
phone: 631-344-4106
cell : 631-681-1596
-
[Star-fst-l] NOVEC from the opened drum is good to use,
Tribedy, Prithwish, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
videbaek, 10/20/2021
- Re: [Star-fst-l] NOVEC from the opened drum is good to use, Aschenauer Elke-Caroline, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Ye, Zhenyu, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Aschenauer Elke-Caroline, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Sharma, Rahul, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Ye, Zhenyu, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
videbaek, 10/20/2021
- Re: [Star-fst-l] NOVEC from the opened drum is good to use, Visser, Gerard, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Visser, Gerard, 10/20/2021
- Re: [Star-fst-l] NOVEC from the opened drum is good to use, Aschenauer Elke-Caroline, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
videbaek, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Ye, Zhenyu, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Sharma, Rahul, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Aschenauer Elke-Caroline, 10/20/2021
- <Possible follow-up(s)>
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
Visser, Gerard, 10/20/2021
- Re: [Star-fst-l] NOVEC from the opened drum is good to use, Ye, Zhenyu, 10/20/2021
-
Re: [Star-fst-l] NOVEC from the opened drum is good to use,
videbaek, 10/20/2021
Archive powered by MHonArc 2.6.24.