Minutes shift change 2023-05-04
general
—————
- Begin-Run party tomorrow noon
- need to temporarily shut down power to racks in rack room at 4:00pm today: 3.2, 4.1, 4.2
- pole tip doors open again
- scaffolding and diving boards going to be installed tomorrow for access to bore: but please keep access to a minimum!
- don’t forget to add your lock to the lock box and remove it right away after finishing work
- working on finishing ORR inspections
- then forward to IRR for approval Monday (1st step)
- reminder: inform shift leader of any work in IR
- Lustre file system back
evening: Xuan
- quiet shift
- INTT work
night: Hanpu
- quiet, only four chiller alarms, acknowledged
- TPC: long pedestal run
- HCal: cosmics running
day: Sookhyun
- alarms, Lee tried to reset, triggered water leak alarm, Lee: likely faulty sensor, Joel: water leak broke sensor, needs to be replaced
- MVTX work to investigate air bubbles
- INTT work on interlock systems
- taking calibration data
- CAD maintenance in gas mixing room triggered alarms
- Tim worked on LV
MBD (Abdul)
- nothing to update
- working on software
HCal (Hanpu)
- taking cosmic runs
- Silas: auto-looping
- will continue until DCM rack shut-down, then hand over to Martin, then take back for Hanpu at midnight
EMcal (Sean)
- more detector development, SiPM bias, bore access
TPOT (John K)
- John K: permission from Hugo to update FELIX firmware to sync with TPC, will do that tonight
- waiting for access to south bore to sure up ground cable
TPC (John K)
- throughput tests with Jin, will continue tonight
INTT (Itaru)
- Steve needs to contact company regarding interlock
- LV and HV on, taking calibration, pedestal data until Raul will arrive
- Rachid: leakage current in silicon detector increased by factor 2, need nitrogen
- Rob is looking into hooking it up to dry air
- requires additional filtering of lab-provided dry air to make it good enough for silicon sensors
MVTX (Zhaozhong)
- Cameron, Yasser working, got signal cable to connect to patch panel 3 and 2E1, wrapped with sleeve
- Aaron and Jeff will install it tomorrow
- daq2 cooling is on bypass: will see high flow rate 10 l/minute
DAQ
- see separate DAQ meeting
(Martin documented firmware issues in GTM and is debugging calorimeter readout)
-
---------------------------------------------------------------------------------
Stefan Bathe
Stefan Bathe
Professor of Physics
Baruch College, CUNY
and RIKEN Visiting Scientist
Baruch: BNL:
17 Lexington Ave Bldg. 510
office 940 office 2-229
phone 646-660-6272 phone 631-344-8490
----------------------------------------------------------------------------------
Baruch College, CUNY
and RIKEN Visiting Scientist
Baruch: BNL:
17 Lexington Ave Bldg. 510
office 940 office 2-229
phone 646-660-6272 phone 631-344-8490
----------------------------------------------------------------------------------
- [Sphenix-run-l] Minutes shift change 2023-05-04, Stefan Bathe, 05/04/2023
Archive powered by MHonArc 2.6.24.